The static loss from flexible corrugated pipe is quite large, something like an order of magnitude more than smooth pipe of the same diameter. Keep
the bends short and you'll be OK. Better yet, go get "wide sweep" fittings. With some care, large radius bends in PVC can be achieved with a hot air
gun and some fixtures and/or assistance. (I must admit I've never done it with anything as large as 100 mm.)
PVC should be just fine for a home lab as long as your not running solvent vapors up the chimney constantly. Some solvent will absorb into the
plastic. It will then desorb with fresh air. So if you use PVC pipe, purge the duct work when you're done with it each time.
Corrugated duct is typically made with vinyl plastic, which I'd worry about more, both because it's thin and it seems to be more subject to solvent
attack. As long as it's on the inlet side of the fan, though, any failure creates another inlet, not a new outlet for hood fumes. Nevertheless, if you
use it, keep it in sight so that you can inspect it.
A side outlet from the hood should be fine if you're using baffles. The baffles will do a lot to distribute the flow sideways across the width of the
hood. |