Regulating a generator? Ye Olde Skewl way?
Think back to the days BEFORE we had solid-state anything, and especially solid-state invertors and power conditioning gear. How did we maintain
60hz, 120 or 240vac?
The thrust of my question is this. Let's say you have a "generator", ie. wire coils moving through a magnetic field. And let's say you have a
waterfall, with a turbine connecting the waterfall to the generator. How do you actually regulate the rotational velocity of the generator, given a
pulsating mechanical energy source, so that you provide a highly consistent frequency from the generator?
The same question could be asked of an all-mechanical diesel or gas engine hooked to an old school generator.
|
|
Magpie
lab constructor
Posts: 5939
Registered: 1-11-2003
Location: USA
Member Is Offline
Mood: Chemistry: the subtle science.
|
|
IIRC they have mechanical "governors." That's about all I can remember.
http://en.wikipedia.org/wiki/Centrifugal_governor
[Edited on 17-2-2010 by Magpie]
The single most important condition for a successful synthesis is good mixing - Nicodem
|
|
bbartlog
International Hazard
Posts: 1139
Registered: 27-8-2009
Location: Unmoored in time
Member Is Offline
Mood: No Mood
|
|
I don't know what the preferred embodiment was at the time of transition to modern electronics, but here's a nice blast from the past, courtesy of
Tesla, which shows an early solution to the problem:
http://www.google.com/patents?vid=511916
|
|
jgourlay
Hazard to Others
Posts: 249
Registered: 9-7-2008
Member Is Offline
Mood: No Mood
|
|
Golden. Absolutely golden fella's. Thanks!
|
|
Contrabasso
Hazard to Others
Posts: 277
Registered: 2-4-2008
Member Is Offline
Mood: No Mood
|
|
Engines were/are regulated by a fan on the flywheel blowing air onto a metal flap that is linked to the throttle to control engine speed, engine speed
controls frequency!
In an old generator there were brushes onto a commutator or sliprings and a controller to feed back some current through the energising winding to
control the rotating magnetic field and the volts output.
In a networked generation system several Alternators will generate synchronously for which there really isnt forum space to discus the detail. However
put simply, if you have a mains generator system and fix a motor to it the motor will turn, now if you actually turn the motor faster that it's
running speed then it will put power back into the network. As long as one alternator is regulated then all the attached synchronous alternators will
hold regulated volts too. However power distribution across different generators may cause uneven and unexpected loading and heating and even
circulating currents. It is done everywhere but it has to be done with care.
|
|
Vogelzang
Banned
Posts: 662
Registered: 26-4-2008
Member Is Offline
Mood: No Mood
|
|
I found one of these.
http://www.google.com/#hl=en&source=hp&q=constant+vo...
|
|
jgourlay
Hazard to Others
Posts: 249
Registered: 9-7-2008
Member Is Offline
Mood: No Mood
|
|
A reply from another website:
Thank you for your enquiry
Automatic speed control of the prime mover, and hence the generator, was originally by mechanical means using centrifugal and other governors.
I don't know whether you "poked" this entry but see here http://www.mpoweruk.com/history.htm#airy for earlier devices.
Early small scale electrical systems were primarily DC systems where the voltage variations were absorbed by the battery.
Before the advent of solid state electronics, high current switching was possible using thyratrons. They were high power tube devices, introduced in
the 1920s, the forerunner of the modern thyristor.
In grid connected systems the generator voltage and frequency are locked to the grid system. Changing the energy output from the prime mover will
cause an equivalent change in the generator output power.
Wave power is a comparatively recent innovation.
I hope this helps
Barrie Lawson.
|
|
weldit
Harmless
Posts: 16
Registered: 29-12-2009
Member Is Offline
Mood: No Mood
|
|
At work we have generators hooked up to motors. They put out DC power. We regulate the voltage with a resistor. I don't know how old school you
want to go but this system has been around for a long time.
|
|
entropy51
Gone, but not forgotten
Posts: 1612
Registered: 30-5-2009
Member Is Offline
Mood: Fissile
|
|
The really old school way was to feed the generator output voltage to an electric clock that had two drive mechanisms. The other drive was
connected to a 60 Hz oscillator that ran off batteries connected to a charger. The turbine operator adjusted the steam admission valve to keep the
clock hands moving in synchrony. This regulated 60 Hz to within a tolerance determined by the operator's attention span and beer intake. Some were
much better at it than others. In those days it was less important that the mains frequency be exactly 60 Hz.
|
|